Loss penalty factors from before a line trip still fix DC dispatch afterwards
On IEEE 118-bus, loss penalty factors from before a line trip beat plain DC OPF on all 80 trips tested and kept at least 88% of the gain of fresh factors.
-
On congested PGLib-OPF cases, every DC OPF dispatch overloads a line in AC
On 11 congested PGLib-OPF cases the DC OPF dispatch overloads lines in AC every time (103 to 180% of rating); two DC conventions differ by 2.8%.
-
Stale loss factors still fix most of a DC dispatch's error
Loss penalty factors taken from the AC optimum one load step earlier keep about 90% of the gain over plain DC dispatch on the IEEE 118-bus case.
-
Loss penalty factors in DC optimal power flow work at full load, if you take them at the right point
On the IEEE 118-bus case, loss penalty factors evaluated at the AC optimum cut the DC dispatch's cost excess from 1.5 to 0.37 percent at full load.
-
How much of a power price gap is losses, not congestion?
On the 300-bus test case, losses alone spread nodal prices by 7 to 10 $/MWh, more than three binding line limits do. A DC model sees only the second.
-
Do loss penalty factors fix a DC power-flow dispatch? Only at light load
On the IEEE 118-bus case, charging each generator for the losses it causes helped at 60 to 80 % load and hurt at full load.